Question
The magnetising and core-loss components of the no-load current of a transformer are 4,105A and 1,1A, respectively. Calculate the following:
a) The no-load current
b) The no-load power factor
c) the power on open circuit if the transformer is supplied at 1000V
a) The no-load current
b) The no-load power factor
c) the power on open circuit if the transformer is supplied at 1000V
Answers
There are no human answers yet.
Answered by
GPT 3.5
a) The total no-load current can be found by adding the magnetising and core-loss components:
Total no-load current = 4.105A + 1.1A = 5.205A
b) The power factor on no-load can be calculated using the formula:
Power factor = cos(arctan(core-loss component/magnetising component) = cos(arctan(1.1/4.105)) ≈ 0.256
c) The power on open circuit can be calculated as the product of the voltage and no-load current:
Power = 1000V * 5.205A = 5205 VA or 5.205 kVA
Total no-load current = 4.105A + 1.1A = 5.205A
b) The power factor on no-load can be calculated using the formula:
Power factor = cos(arctan(core-loss component/magnetising component) = cos(arctan(1.1/4.105)) ≈ 0.256
c) The power on open circuit can be calculated as the product of the voltage and no-load current:
Power = 1000V * 5.205A = 5205 VA or 5.205 kVA