an electric oven of 2kW power heating is operated in a domestic circuit that has a current rating 5A. If the supply voltage is 220V. What result do you expect? Explain
Answers
Answered by
Henry
P = V*I = 2000 W.
220I = 2000
I = 9.09 Amps.
The current too high for the circuit.
If the circuit is properly protected, the fuse will blow or the circuit breaker will trip.
220I = 2000
I = 9.09 Amps.
The current too high for the circuit.
If the circuit is properly protected, the fuse will blow or the circuit breaker will trip.